hello, we have a ATR 141 device for using the 4-20mA linear signal (pressure sensor input for 0 to 1600 mbar), we want a output which will be activated at 190 mbar and deactivated at 210mbar. which are the settings of set point and hysteresis.
Please guide us accordingly.
Thanks in advance.
[ATR141] Input 4-20mA and hysteresis of regulation
-
- Moderatore
- Posts: 1702
- Joined: 29/10/2010, 10:09
- Contact:
Re: ATR 141 configure
Hi,
you have to set:
setpoint "210"
command Hysteresis: "20"
you have to set:
setpoint "210"
command Hysteresis: "20"