Iris _

Pixsys Forum

everybody's effort for the same goal

[ATR141] Input 4-20mA and hysteresis of regulation

Post Reply
user4242
Posts: 2
Joined: 31/10/2012, 11:35

[ATR141] Input 4-20mA and hysteresis of regulation

Post by user4242 »

hello, we have a ATR 141 device for using the 4-20mA linear signal (pressure sensor input for 0 to 1600 mbar), we want a output which will be activated at 190 mbar and deactivated at 210mbar. which are the settings of set point and hysteresis.
Please guide us accordingly.
Thanks in advance.
Pixsys tecnico 1
Moderatore
Posts: 1737
Joined: 29/10/2010, 10:09
Contact:

Re: ATR 141 configure

Post by Pixsys tecnico 1 »

Hi,
you have to set:
setpoint "210"
command Hysteresis: "20"
user4242
Posts: 2
Joined: 31/10/2012, 11:35

Re: ATR 141 configure

Post by user4242 »

Thanks a lot...
Post Reply