Iris _

Pixsys Forum

everybody's effort for the same goal

[ATR401] Temperature and humidity control Probe[2000.50.021]

Post Reply
user17801
Posts: 1
Joined: 14/08/2018, 11:54

[ATR401] Temperature and humidity control Probe[2000.50.021]

Post by user17801 »

This application allows you to control the temperature and humidity using a PT100 signal on AI1 and a 0-10V signal on AI2 of the ATR401-24ABC controller. The regulation is in hot mode and is ON / OFF with 5 ° C of hysteresis on the temperature setpoint (relay Q1).
Alarm 1 is in absolute value and is activated above the set point with a hysteresis of 1 ° C for process 1 (temperature).
Alarm 2 is in absolute value and is activated above the setpoint with a hysteresis of 1% for process 2 (humidity).
The probe used is 2000.50.021. (Https://www.pixsys.net/it/prodotti/tras ... sm-umidita)

Electrical connections of the regulator towards the probe in question:
Signal AI1 (PT100)
PIN11 -> blue thread
PIN12 -> brown thread
PIN13 -> white thread
AI2 signal (0-10V)
PIN14 -> yellow / green thread
PIN15 -> black thread
PIN17 -> red thread
Pixsys tecnico 6
Moderatore
Posts: 1218
Joined: 12/09/2016, 14:49

Re: [ATR401] Temperature and humidity control Probe 2000.50.

Post by Pixsys tecnico 6 »

Hi,
LabSoftview files and example print screen attached.
ATR401_pt100_0_10V.PNG
Best regards.
You do not have the required permissions to view the files attached to this post.