This application allows you to control the temperature and humidity using a PT100 signal on AI1 and a 0-10V signal on AI2 of the ATR401-24ABC controller. The regulation is in hot mode and is ON / OFF with 5 ° C of hysteresis on the temperature setpoint (relay Q1).
Alarm 1 is in absolute value and is activated above the set point with a hysteresis of 1 ° C for process 1 (temperature).
Alarm 2 is in absolute value and is activated above the setpoint with a hysteresis of 1% for process 2 (humidity).
The probe used is 2000.50.021. (Https://www.pixsys.net/it/prodotti/tras ... sm-umidita)
Electrical connections of the regulator towards the probe in question:
Signal AI1 (PT100)
PIN11 -> blue thread
PIN12 -> brown thread
PIN13 -> white thread
AI2 signal (0-10V)
PIN14 -> yellow / green thread
PIN15 -> black thread
PIN17 -> red thread
[ATR401] Temperature and humidity control Probe[2000.50.021]
-
user17801
- Posts: 1
- Joined: 14/08/2018, 11:54
-
Pixsys tecnico 6
- Moderatore
- Posts: 1218
- Joined: 12/09/2016, 14:49
Re: [ATR401] Temperature and humidity control Probe 2000.50.
Hi,
LabSoftview files and example print screen attached.
Best regards.
LabSoftview files and example print screen attached.
Best regards.