Dear mrs, mr,
I am using a ATR234-20ABC.
This device is connected with a drew point sensor 2 wire 4.20mA
I can see the value on the controller .
But I need to transert this value with the Controller Output C1 in 4.20mA
My configuration is
2 - Sen {4.20}
3 - dP {0.0}
4 - LoLS {-100}
5 - uPLS {20}
1 - cout {c4.20}
67 rEtr {MA P}
68 LoLr {0}
69 UPLr {100}
jumpers are on JP5 an JP7 JP9 0-- (as picture 5.1.j)
The controller is unable to activate the C1 output
Is it a controller s problem ? configuration problem ?
Best regards
renaud
Unable to activate Output1 in 4.20mA
-
Pixsys tecnico 6
- Moderatore
- Posts: 1218
- Joined: 12/09/2016, 14:49
Re: Unable to activate Output1 in 4.20mA
Hi,
this is a configuration parameter issue: the parameter 1.[cout] must be "c.01" value if you want use the retransmission function. Please check it.
Best regards.
this is a configuration parameter issue: the parameter 1.[cout] must be "c.01" value if you want use the retransmission function. Please check it.
Best regards.
You do not have the required permissions to view the files attached to this post.
-
ren973
- Posts: 3
- Joined: 20/03/2019, 3:41
Re: Unable to activate Output1 in 4.20mA
Dear Mr
I changed the parameter as you said ... But still not working
C1 is still off
Best regards
renaud
I changed the parameter as you said ... But still not working
C1 is still off
Best regards
renaud
-
Pixsys tecnico 6
- Moderatore
- Posts: 1218
- Joined: 12/09/2016, 14:49
Re: Unable to activate Output1 in 4.20mA
Hi,
parameters list and hardware configuration attached.
If it does not work fine using this settings, please contacts your reseller.
Best Regards.
parameters list and hardware configuration attached.
If it does not work fine using this settings, please contacts your reseller.
Best Regards.
You do not have the required permissions to view the files attached to this post.
-
ren973
- Posts: 3
- Joined: 20/03/2019, 3:41
Re: Unable to activate Output1 in 4.20mA
Thank you for your help