Iris _

Pixsys Forum

everybody's effort for the same goal

Unable to activate Output1 in 4.20mA

Post Reply
ren973
Posts: 3
Joined: 20/03/2019, 3:41

Unable to activate Output1 in 4.20mA

Post by ren973 »

Dear mrs, mr,
I am using a ATR234-20ABC.

This device is connected with a drew point sensor 2 wire 4.20mA
I can see the value on the controller .

But I need to transert this value with the Controller Output C1 in 4.20mA

My configuration is

2 - Sen {4.20}
3 - dP {0.0}
4 - LoLS {-100}
5 - uPLS {20}


1 - cout {c4.20}
67 rEtr {MA P}
68 LoLr {0}
69 UPLr {100}

jumpers are on JP5 an JP7 JP9 0-- (as picture 5.1.j)

The controller is unable to activate the C1 output
Is it a controller s problem ? configuration problem ?
Best regards
renaud
Pixsys tecnico 6
Moderatore
Posts: 1212
Joined: 12/09/2016, 14:49

Re: Unable to activate Output1 in 4.20mA

Post by Pixsys tecnico 6 »

Hi,
this is a configuration parameter issue: the parameter 1.[cout] must be "c.01" value if you want use the retransmission function. Please check it.

Best regards.
You do not have the required permissions to view the files attached to this post.
ren973
Posts: 3
Joined: 20/03/2019, 3:41

Re: Unable to activate Output1 in 4.20mA

Post by ren973 »

Dear Mr
I changed the parameter as you said ... But still not working
C1 is still off

Best regards
renaud
Pixsys tecnico 6
Moderatore
Posts: 1212
Joined: 12/09/2016, 14:49

Re: Unable to activate Output1 in 4.20mA

Post by Pixsys tecnico 6 »

Hi,
parameters list and hardware configuration attached.
If it does not work fine using this settings, please contacts your reseller.

Best Regards.
You do not have the required permissions to view the files attached to this post.
ren973
Posts: 3
Joined: 20/03/2019, 3:41

Re: Unable to activate Output1 in 4.20mA

Post by ren973 »

Thank you for your help
Post Reply