[ATR141] Input 4-20mA and hysteresis of regulation

Posted: 31/10/2012, 12:19
by user4242
hello, we have a ATR 141 device for using the 4-20mA linear signal (pressure sensor input for 0 to 1600 mbar), we want a output which will be activated at 190 mbar and deactivated at 210mbar. which are the settings of set point and hysteresis.
Please guide us accordingly.
Thanks in advance.

Re: ATR 141 configure

Posted: 31/10/2012, 12:43
by Pixsys tecnico 1
Hi,
you have to set:
setpoint "210"
command Hysteresis: "20"

Re: ATR 141 configure

Posted: 31/10/2012, 12:54
by user4242
Thanks a lot...