Page 1 of 1
[Atr444-22ABC] Remote setpoint
Posted: 29/05/2026, 9:41
by Jac
Good morning, i have difficulties with enabling the Remote setpoint function as wanted. (A2) p19 A.in2 is set on 0-10V. (B2) p61 c.Pr.2 is set on A.iN.2 and p62 rEN.S. is set on ENAB. What i wanted is to use the digital input 1 for changing the remote setpoint to local. (E1) p275 d.i.I.F states in the manual it has the function REM.S.E. But when i scan the ATR444-22abc it is not listed as an option. The list stops at SEt.K. Could someone explain to me how it works or if i have missed a setting.
Thank you in advance,
Roy Termaat
Re: [Atr444-22ABC] Remote setpoint
Posted: 03/06/2026, 15:10
by Pixsys tecnico 7
Good morning,
it seems that the voice you are looking for is missing in our app and PC programmation tool. The issue will be resolved in both future versions.
Have you already tried configuring p275 parameter by buttons, directly on instrument?
Doing so, you should see the correct voices on that parameter.
Below the correct procedure to access and modify the configuration parameters directly on the instrument:
press "FNC" for 3 seconds;
enter the password "1234";
press "FNC" again to confirm;
use the two arrows to scroll through the parameter groups;
press "SET" to allow modification of the selected parameter;
use the arrows to change its property;
press "SET" again to confirm the change;
Press "FNC" once to return to parameter group selection,
Press "FNC" a second time to exit setup mode.