Good morning, i have difficulties with enabling the Remote setpoint function as wanted. (A2) p19 A.in2 is set on 0-10V. (B2) p61 c.Pr.2 is set on A.iN.2 and p62 rEN.S. is set on ENAB. What i wanted is to use the digital input 1 for changing the remote setpoint to local. (E1) p275 d.i.I.F states in the manual it has the function REM.S.E. But when i scan the ATR444-22abc it is not listed as an option. The list stops at SEt.K. Could someone explain to me how it works or if i have missed a setting.
Thank you in advance,
Roy Termaat
[Atr444-22ABC] Remote setpoint
Jump to
- Forum Italiano
- ↳ Argomenti Generali
- ↳ FAQ Regolatori e Termoregolatori
- ↳ FAQ Controllori di processo / Programmatori a step
- ↳ FAQ PLC, HMi e Interfacce
- ↳ HMI LogicLab - Movicon (TD410, TD710, TD810, TD820)
- ↳ PLC LogicLab (PL280, PL500, PL600)
- ↳ PLC e HMI Codesys (PL700, TC6xx, TC8xx)
- ↳ PanelPC (PC800, PC815, PC820, PC830)
- ↳ WebPanel (WPxxx)
- ↳ Moduli I/O e convertitori
- ↳ PLC e HMI PlProg - TdDesigner (EPL101, PL250, PL260, TD240, TD320)
- ↳ HMI LogicLab - PageLab (TDxxx, TY5xx, TY7xx)
- ↳ FAQ sonde e ssr
- ↳ FAQ Timer / Contatori / Tachimetri
- ↳ FAQ Inverter
- English Forum
- ↳ General Topics
- ↳ FAQ controllers
- ↳ FAQ Process controllers / Steps controllers
- ↳ FAQ PLC, HMI and Interfaces
- ↳ HMI LogicLab - Movicon (TD410, TD710, TD810, TD820)
- ↳ PLC LogicLab (PL280, PL500, PL600)
- ↳ PLC and HMI Codesys (PL700, TC6xx, TC8xx)
- ↳ PanelPC (PC800, PC815, PC820, PC830)
- ↳ WebPanel (WPxxx)
- ↳ I/O modules and converters
- ↳ PLC and HMI PlProg - TdDesigner (EPL101, PL250, PL260, TD240, TD320)
- ↳ HMI LogicLab - PageLab (TDxxx, TY5xx, TY7xx)
- ↳ FAQ sensors and SSR
- ↳ FAQ Timers / Counters / Tachometers
- ↳ FAQ Inverter