Page 1 of 1

[ATR244-12ABC] Humidify/dry inverse voltage

Posted: 20/03/2022, 13:06
by leandromarceddu
Hi

I'm trying to configure an ATR244-12ABC like this:

AI1 = 4-20mA sensor, RH transmitter
DO = Relay
Setpunt = 50
Q1 = closed in 0-50 range (Q2 open)
Q2 = closed in 50-100 range (Q1 open)
AO1 = Output in 0-10V. Only active when Q1 = closed. This takes the value of AI1 and inverses it: for example AI = 10 (on scale of 0-50) it should output 8V. (50-10 = 40 x 2 = 80 = 8V)
This does not seem possible? I have also trouble programming this. I'm using labsoftview and mypixsys but mypixsys corrupts the settings.

EDIT: forgot to include atr.

Re: [ATR244-12ABC] Humidify/dry inverse voltage

Posted: 21/03/2022, 9:59
by Pixsys tecnico 6
Hi,
I edited your file . atr with the MyPixsys app without any problems.
Try testing the file I sent you on your phone.

The atr. file includes all the required functions. The "DO=Relay" has been activated associated with the alarm 3 "AL.3" as active above and deactivated below.

The program it should work as required.
Par.35 [c.ou.1] > "0-10V":
Immagine 2022-03-21 095212.png
Best Regards

Re: [ATR244-12ABC] Humidify/dry inverse voltage

Posted: 21/03/2022, 16:20
by leandromarceddu
Pixsys tecnico 6 wrote:Hi,
I edited your file . atr with the MyPixsys app without any problems.
Try testing the file I sent you on your phone.

The atr. file includes all the required functions. The "DO=Relay" has been activated associated with the alarm 3 "AL.3" as active above and deactivated below.

The program it should work as required.
Par.35 [c.ou.1] > "0-10V":
Immagine 2022-03-21 095212.png
Best Regards
Hi, loading your file into labsoftview gives me an error about it being created in an older version, I'll only do it on the phone for now.

Second, this seems to work, however can I use the setpoint (configured in LabSoftView to 50) to control the upper and lower limits for AL1/2/3? Or do they all have seperate setpoints?

Re: [ATR244-12ABC] Humidify/dry inverse voltage

Posted: 21/03/2022, 16:33
by Pixsys tecnico 6
Hi,
Second, this seems to work, however can I use the setpoint (configured in LabSoftView to 50) to control the upper and lower limits for AL1/2/3? Or do they all have seperate setpoints?
Yes, it's possible.
Now AL.1,AL.2 and AL.3 are associated with setpoint 1.
In the old configuration each alarm had its own separate setpoint.

Best Regards

Re: [ATR244-12ABC] Humidify/dry inverse voltage

Posted: 21/03/2022, 17:04
by leandromarceddu
Pixsys tecnico 6 wrote:Hi,
Second, this seems to work, however can I use the setpoint (configured in LabSoftView to 50) to control the upper and lower limits for AL1/2/3? Or do they all have seperate setpoints?
Yes, it's possible.
Now AL.1,AL.2 and AL.3 are associated with setpoint 1.
In the old configuration each alarm had its own separate setpoint.

Best Regards
Thanks! This was very helpful; I've changed alarm 1 and 3 to Lo.dEV. to be correct and this works.

To make the controller only work when DI1 is closed (V+ connected to DI1), do I select Run or Start/stop?

Re: [ATR244-12ABC] Humidify/dry inverse voltage

Posted: 21/03/2022, 17:32
by Pixsys tecnico 6
hi,
you’ll have to set it as "RUN".

Best Regards

Re: [ATR244-12ABC] Humidify/dry inverse voltage

Posted: 23/09/2022, 11:22
by leandromarceddu
Hi.

Sorry for the old topic revive, but still having issues with this.

Currently the humidifying state has been set to AL1 and AL3.
Drying is set to AL2.

Both fases trigger correctly (at 55% relative humidity).

However AL3 does not seem to output any 0-10Vdc signal, why is this?

Re: [ATR244-12ABC] Humidify/dry inverse voltage

Posted: 28/09/2022, 16:32
by leandromarceddu
This problem is still on-going, any advice?

Re: [ATR244-12ABC] Humidify/dry inverse voltage

Posted: 28/09/2022, 17:05
by Pixsys tecnico 6
Good morning,
As you can see from the image below, alarm 3 is associated with digital output DO1 and not 0-10V.
From your configuration the output 0-10V is associated with the command output Par.35 [c.ou.1].
image.jpg
Best regards

Re: [ATR244-12ABC] Humidify/dry inverse voltage

Posted: 29/09/2022, 9:31
by leandromarceddu
Pixsys tecnico 6 wrote:Good morning,
As you can see from the image below, alarm 3 is associated with digital output DO1 and not 0-10V.
From your configuration the output 0-10V is associated with the command output Par.35 [c.ou.1].
image.jpg
Best regards
Good morning.

Thanks for the clarification.
However then what am I doing wrong at the moment? There is no 0-10V output from AO1 under 55 (u.L.S.1) par. 41.

Re: [ATR244-12ABC] Humidify/dry inverse voltage

Posted: 29/09/2022, 12:49
by Pixsys tecnico 6
The problem is that you have enabled the retransmission (0-10V) of the AL1 threshold in parameter 298 [rt.M1] and the command output Par.35 [c.ou.1] to "c.0-10".
You can’t have both functions at once, you can only use them one at a time.
You will need to disable par.298 if you want the analogue output to work.

Best regards