[ATR244-12ABC] Humidify/dry inverse voltage
-
leandromarceddu
- Posts: 6
- Joined: 12/01/2022, 16:39
[ATR244-12ABC] Humidify/dry inverse voltage
Hi
I'm trying to configure an ATR244-12ABC like this:
AI1 = 4-20mA sensor, RH transmitter
DO = Relay
Setpunt = 50
Q1 = closed in 0-50 range (Q2 open)
Q2 = closed in 50-100 range (Q1 open)
AO1 = Output in 0-10V. Only active when Q1 = closed. This takes the value of AI1 and inverses it: for example AI = 10 (on scale of 0-50) it should output 8V. (50-10 = 40 x 2 = 80 = 8V)
This does not seem possible? I have also trouble programming this. I'm using labsoftview and mypixsys but mypixsys corrupts the settings.
EDIT: forgot to include atr.
I'm trying to configure an ATR244-12ABC like this:
AI1 = 4-20mA sensor, RH transmitter
DO = Relay
Setpunt = 50
Q1 = closed in 0-50 range (Q2 open)
Q2 = closed in 50-100 range (Q1 open)
AO1 = Output in 0-10V. Only active when Q1 = closed. This takes the value of AI1 and inverses it: for example AI = 10 (on scale of 0-50) it should output 8V. (50-10 = 40 x 2 = 80 = 8V)
This does not seem possible? I have also trouble programming this. I'm using labsoftview and mypixsys but mypixsys corrupts the settings.
EDIT: forgot to include atr.
You do not have the required permissions to view the files attached to this post.
-
Pixsys tecnico 6
- Moderatore
- Posts: 1219
- Joined: 12/09/2016, 14:49
Re: [ATR244-12ABC] Humidify/dry inverse voltage
Hi,
I edited your file . atr with the MyPixsys app without any problems.
Try testing the file I sent you on your phone.
The atr. file includes all the required functions. The "DO=Relay" has been activated associated with the alarm 3 "AL.3" as active above and deactivated below.
The program it should work as required.
Par.35 [c.ou.1] > "0-10V": Best Regards
I edited your file . atr with the MyPixsys app without any problems.
Try testing the file I sent you on your phone.
The atr. file includes all the required functions. The "DO=Relay" has been activated associated with the alarm 3 "AL.3" as active above and deactivated below.
The program it should work as required.
Par.35 [c.ou.1] > "0-10V": Best Regards
You do not have the required permissions to view the files attached to this post.
-
leandromarceddu
- Posts: 6
- Joined: 12/01/2022, 16:39
Re: [ATR244-12ABC] Humidify/dry inverse voltage
Hi, loading your file into labsoftview gives me an error about it being created in an older version, I'll only do it on the phone for now.Pixsys tecnico 6 wrote:Hi,
I edited your file . atr with the MyPixsys app without any problems.
Try testing the file I sent you on your phone.
The atr. file includes all the required functions. The "DO=Relay" has been activated associated with the alarm 3 "AL.3" as active above and deactivated below.
The program it should work as required.
Par.35 [c.ou.1] > "0-10V": Best Regards
Second, this seems to work, however can I use the setpoint (configured in LabSoftView to 50) to control the upper and lower limits for AL1/2/3? Or do they all have seperate setpoints?
-
Pixsys tecnico 6
- Moderatore
- Posts: 1219
- Joined: 12/09/2016, 14:49
Re: [ATR244-12ABC] Humidify/dry inverse voltage
Hi,
Second, this seems to work, however can I use the setpoint (configured in LabSoftView to 50) to control the upper and lower limits for AL1/2/3? Or do they all have seperate setpoints?
Yes, it's possible.
Now AL.1,AL.2 and AL.3 are associated with setpoint 1.
In the old configuration each alarm had its own separate setpoint.
Best Regards
Second, this seems to work, however can I use the setpoint (configured in LabSoftView to 50) to control the upper and lower limits for AL1/2/3? Or do they all have seperate setpoints?
Yes, it's possible.
Now AL.1,AL.2 and AL.3 are associated with setpoint 1.
In the old configuration each alarm had its own separate setpoint.
Best Regards
You do not have the required permissions to view the files attached to this post.
-
leandromarceddu
- Posts: 6
- Joined: 12/01/2022, 16:39
Re: [ATR244-12ABC] Humidify/dry inverse voltage
Thanks! This was very helpful; I've changed alarm 1 and 3 to Lo.dEV. to be correct and this works.Pixsys tecnico 6 wrote:Hi,
Second, this seems to work, however can I use the setpoint (configured in LabSoftView to 50) to control the upper and lower limits for AL1/2/3? Or do they all have seperate setpoints?
Yes, it's possible.
Now AL.1,AL.2 and AL.3 are associated with setpoint 1.
In the old configuration each alarm had its own separate setpoint.
Best Regards
To make the controller only work when DI1 is closed (V+ connected to DI1), do I select Run or Start/stop?
You do not have the required permissions to view the files attached to this post.
-
Pixsys tecnico 6
- Moderatore
- Posts: 1219
- Joined: 12/09/2016, 14:49
Re: [ATR244-12ABC] Humidify/dry inverse voltage
hi,
you’ll have to set it as "RUN".
Best Regards
you’ll have to set it as "RUN".
Best Regards
-
leandromarceddu
- Posts: 6
- Joined: 12/01/2022, 16:39
Re: [ATR244-12ABC] Humidify/dry inverse voltage
Hi.
Sorry for the old topic revive, but still having issues with this.
Currently the humidifying state has been set to AL1 and AL3.
Drying is set to AL2.
Both fases trigger correctly (at 55% relative humidity).
However AL3 does not seem to output any 0-10Vdc signal, why is this?
Sorry for the old topic revive, but still having issues with this.
Currently the humidifying state has been set to AL1 and AL3.
Drying is set to AL2.
Both fases trigger correctly (at 55% relative humidity).
However AL3 does not seem to output any 0-10Vdc signal, why is this?
You do not have the required permissions to view the files attached to this post.
-
leandromarceddu
- Posts: 6
- Joined: 12/01/2022, 16:39
Re: [ATR244-12ABC] Humidify/dry inverse voltage
This problem is still on-going, any advice?
-
Pixsys tecnico 6
- Moderatore
- Posts: 1219
- Joined: 12/09/2016, 14:49
Re: [ATR244-12ABC] Humidify/dry inverse voltage
Good morning,
As you can see from the image below, alarm 3 is associated with digital output DO1 and not 0-10V.
From your configuration the output 0-10V is associated with the command output Par.35 [c.ou.1]. Best regards
As you can see from the image below, alarm 3 is associated with digital output DO1 and not 0-10V.
From your configuration the output 0-10V is associated with the command output Par.35 [c.ou.1]. Best regards
You do not have the required permissions to view the files attached to this post.
-
leandromarceddu
- Posts: 6
- Joined: 12/01/2022, 16:39
Re: [ATR244-12ABC] Humidify/dry inverse voltage
Good morning.Pixsys tecnico 6 wrote:Good morning,
As you can see from the image below, alarm 3 is associated with digital output DO1 and not 0-10V.
From your configuration the output 0-10V is associated with the command output Par.35 [c.ou.1]. Best regards
Thanks for the clarification.
However then what am I doing wrong at the moment? There is no 0-10V output from AO1 under 55 (u.L.S.1) par. 41.
-
Pixsys tecnico 6
- Moderatore
- Posts: 1219
- Joined: 12/09/2016, 14:49
Re: [ATR244-12ABC] Humidify/dry inverse voltage
The problem is that you have enabled the retransmission (0-10V) of the AL1 threshold in parameter 298 [rt.M1] and the command output Par.35 [c.ou.1] to "c.0-10".
You can’t have both functions at once, you can only use them one at a time.
You will need to disable par.298 if you want the analogue output to work.
Best regards
You can’t have both functions at once, you can only use them one at a time.
You will need to disable par.298 if you want the analogue output to work.
Best regards