Re: [ATR244-12ABC] Humidify/dry inverse voltage

Posted: 29/09/2022, 12:49
by Pixsys tecnico 6
The problem is that you have enabled the retransmission (0-10V) of the AL1 threshold in parameter 298 [rt.M1] and the command output Par.35 [c.ou.1] to "c.0-10".
You can’t have both functions at once, you can only use them one at a time.
You will need to disable par.298 if you want the analogue output to work.

Best regards