Hello,
I did not find a related topic on this subject. I am using an atr 144 controller on a simple heating application. Everything works OK, the only problem is the output of alarm 2. It is connected on PIN 6 and 7. When the Proccess value goes over 50 I would like to turn on alarm 2, so I get 24 V on PIN 6.
What parameters should I set so I can achine the desired result.
Thank you for your answer in advance.
Problem with alarm 2 output on atr 144
-
- Moderatore
- Posts: 1203
- Joined: 12/09/2016, 14:49
Re: Problem with alarm 2 output on atr 144
Good Morning,
To activate the alarm associated with Q2, you must set in Group D [AL.1]> Par.62 [AL.1.F. ]> "Ab.uP.A." only if in Group B [cmd.1]> Par.18 [c.ou.1] is set to "c.O1".
To set the threshold must exit the configuration and press SET.
BR,
To activate the alarm associated with Q2, you must set in Group D [AL.1]> Par.62 [AL.1.F. ]> "Ab.uP.A." only if in Group B [cmd.1]> Par.18 [c.ou.1] is set to "c.O1".
To set the threshold must exit the configuration and press SET.
BR,