Post by Pixsys tecnico 6 »

This application allows you to distribute the command on relay Q1 and Q2. When the output command on contact Q1 is active it will alternate with Q2 for the time set on parameter P_70.[A1dE] using a time base of minutes. In addition, digital input 1 is used to make the season change.

ATR144-12ABC I/O Connections:
PIN 1-2 --> Power supply
PIN 4-5 --> Q1 relay used for actuator 1
PIN 6-7 --> Q2 relay used for actuator 2 (alternating with Q1 for the time set on P_70 and when activating the ATR144 shows the custom message set on parameter P_72)
PIN 8-9 --> Digital input 1 for season change (open=heating, closed=cooling)
PIN 10-11-12 --> PT100 probe input
atr144-abc_config.pdf
pixsys_atr144-abc_backup.zip
Best regards.