[TD320] Using with EPL101 as I/O module

Posted: 30/01/2012, 14:11
by user2474
I have TD320 and epl101
I need to use TD320 like a controller and EPL101 as I/O module.
1. How i need configure (connect o progamming) EPL101.
2. How i can reach I/O ports and it's configurations (addresses, registers...) from TD320
Thank you

Re: TD320&EPL101

Posted: 30/01/2012, 15:11
by Pixsys tecnico 2
In the attached file to the message is an example of the configuration of TD320 and EPL101 communication.

connections TD320 problems

Posted: 08/02/2012, 15:58
by user2474
Sorry more one time
All my efforts to communicate TD320 with epl101 fail
I тried rs482 and rs232
communication LED lid , but i can't write or read from slave
may be necessary some additional configuration?
I connect TD320 with EPL101 via RS485 EXP_1 address 3 and othe EPL101 via RS232 COM1 address 2
it was checked with 2 different DP320
in this configuration i sometimes see wrong changes in " read 110" position
Can you help me find my mistakes?
this is my configuration:
from PC via RS485 I can rich and change registers in TD320 or EPL101

Re: connections TD320 problems

Posted: 08/02/2012, 17:27
by Pixsys tecnico 2
Hello,
the problem is the index of COM_ and EXP_ command.
The index must be different every COM_ and EXP_ command, the first is COM_1, the second is COM_2 and keep going like this.
The correct file is link to this message.

Re: connections TD320 problems

Posted: 09/02/2012, 14:04
by user2474
Thank you.
Everything is work good exept AI inputs.
Can you show me how configure AI1 - AI4 for NTC 10K probe ?
Is it necessary configure MIN, MAX, OFFSET, and GAIN ?
SM40 (2040) - SM43(2043) set to 15 (NTC 10K)
JP2, JP3, JP4 are set, 1,28V on AI1 (NTC 10K probe connect) ; 2,5V AI2-AI4 contacts(open)
I see AI1 - AI4 DISABLE (SM60-SM63 EPL101 PC monitoring)