[TD320] Using with EPL101 as I/O module

Post Reply
user2474
Posts: 3
Joined: 20/01/2012, 9:10

[TD320] Using with EPL101 as I/O module

Post by user2474 »

I have TD320 and epl101
I need to use TD320 like a controller and EPL101 as I/O module.
1. How i need configure (connect o progamming) EPL101.
2. How i can reach I/O ports and it's configurations (addresses, registers...) from TD320
Thank you
Pixsys tecnico 2
Moderatore
Posts: 135
Joined: 16/12/2010, 17:46

Re: TD320&EPL101

Post by Pixsys tecnico 2 »

In the attached file to the message is an example of the configuration of TD320 and EPL101 communication.
You do not have the required permissions to view the files attached to this post.
user2474
Posts: 3
Joined: 20/01/2012, 9:10

connections TD320 problems

Post by user2474 »

Sorry more one time
All my efforts to communicate TD320 with epl101 fail
I тried rs482 and rs232
communication LED lid , but i can't write or read from slave
may be necessary some additional configuration?
I connect TD320 with EPL101 via RS485 EXP_1 address 3 and othe EPL101 via RS232 COM1 address 2
it was checked with 2 different DP320
in this configuration i sometimes see wrong changes in " read 110" position
Can you help me find my mistakes?
this is my configuration:
from PC via RS485 I can rich and change registers in TD320 or EPL101
You do not have the required permissions to view the files attached to this post.
Pixsys tecnico 2
Moderatore
Posts: 135
Joined: 16/12/2010, 17:46

Re: connections TD320 problems

Post by Pixsys tecnico 2 »

Hello,
the problem is the index of COM_ and EXP_ command.
The index must be different every COM_ and EXP_ command, the first is COM_1, the second is COM_2 and keep going like this.
The correct file is link to this message.
You do not have the required permissions to view the files attached to this post.
user2474
Posts: 3
Joined: 20/01/2012, 9:10

Re: connections TD320 problems

Post by user2474 »

Thank you.
Everything is work good exept AI inputs.
Can you show me how configure AI1 - AI4 for NTC 10K probe ?
Is it necessary configure MIN, MAX, OFFSET, and GAIN ?
SM40 (2040) - SM43(2043) set to 15 (NTC 10K)
JP2, JP3, JP4 are set, 1,28V on AI1 (NTC 10K probe connect) ; 2,5V AI2-AI4 contacts(open)
I see AI1 - AI4 DISABLE (SM60-SM63 EPL101 PC monitoring)
You do not have the required permissions to view the files attached to this post.