[ATR121] as simple indicator
- 
			
					user54
 - Posts: 3
 - Joined: 10/12/2010, 13:53
 
[ATR121] as simple indicator
Can I use the ATR121 as simple indicator ? No command output is required, just sensor reading and display
						
									
						
										
							- 
			
					Pixsys tecnico 1
 - Moderatore
 - Posts: 1721
 - Joined: 29/10/2010, 10:09
 - Contact:
 
Re: ATR121
First of all select the proper sensor type on parameter 2 "sen"
To avoid the clicking of relays , set the parameter 28 "Fnc" as "vIS" : this option will deactivate both relay outputs and the unit will operate as simple indicator.
						
									
						
										
							To avoid the clicking of relays , set the parameter 28 "Fnc" as "vIS" : this option will deactivate both relay outputs and the unit will operate as simple indicator.
- 
			
					user497
 - Posts: 36
 - Joined: 09/02/2011, 14:33
 - Location: Latvia
 - Contact:
 
Re: ATR121 as simple indicator
Can ATR121 do this:
At start up start to heat up till 60C ( with on/off ) and after reaching this set point ( 60C) turns off output and goes down till lowest outside temperature ( by us -25C ).
With big hysteresis i can not get it, because if i turn the device on and the outside temperature ( ~ 20C ) in this case is in range = setpoint ( 60C) - hysteresis ( 50C ), then the output is off, and wait for lower temperature to turn it on! If outside temperature ( ~20C) is out of range = setpoint ( 60C) - hysteresis ( 30C ), then controller turns on output and start to heat!
I need to make process: independent of process temperature after turning the controller on, it starts to heat and is going to reach the set point! ( without PID ). And after reaching the setpoint turns off, and no matter, how low it goes,it doesnt turn on!
						
									
						
										
							At start up start to heat up till 60C ( with on/off ) and after reaching this set point ( 60C) turns off output and goes down till lowest outside temperature ( by us -25C ).
With big hysteresis i can not get it, because if i turn the device on and the outside temperature ( ~ 20C ) in this case is in range = setpoint ( 60C) - hysteresis ( 50C ), then the output is off, and wait for lower temperature to turn it on! If outside temperature ( ~20C) is out of range = setpoint ( 60C) - hysteresis ( 30C ), then controller turns on output and start to heat!
I need to make process: independent of process temperature after turning the controller on, it starts to heat and is going to reach the set point! ( without PID ). And after reaching the setpoint turns off, and no matter, how low it goes,it doesnt turn on!