Page 1 of 1

[DRR245-ABC-T] as signal converter (TcK to 0-10Volt)

Posted: 27/12/2010, 16:14
by user54
Which parameters should I set in order to use the unit as a SIGNAL CONVERTER (thermocouple K to 0-10Volt) :?:

Re: Controller DRR245

Posted: 28/12/2010, 12:48
by Pixsys tecnico 1
For the requested application please set the following parameters as indicated :
"c.out": c.o1
"sen": tc.K
"rEtr": vo.P
"LoL.r": -260
"uPLi.r": 1360

This way the retransmission output limits will be 0 Volt for -260°C and 10Volt for +1360°C. This is corresponding to the measuring range of thermocouple K. If you want to change these limits , you may act on parameters "LoL.r" and "uPLi.r".

Do not forget to short-circuit pins 9 and 10 in order to enable the 0-10Volt output!

Re: [DRR245-ABC-T] as signal converter (TcK to 0-10Volt)

Posted: 27/07/2011, 9:50
by user497
Is 4...20mA output passive or active from DRR245?

I want to connect it to PLC analog input.

Grazie!

Re: [DRR245-ABC-T] as signal converter (TcK to 0-10Volt)

Posted: 08/08/2011, 9:26
by Pixsys tecnico 1
Is an active output.