[DRR245-ABC-T] as signal converter (TcK to 0-10Volt)
-
- Posts: 3
- Joined: 10/12/2010, 13:53
[DRR245-ABC-T] as signal converter (TcK to 0-10Volt)
Which parameters should I set in order to use the unit as a SIGNAL CONVERTER (thermocouple K to 0-10Volt)
-
- Moderatore
- Posts: 1702
- Joined: 29/10/2010, 10:09
- Contact:
Re: Controller DRR245
For the requested application please set the following parameters as indicated :
"c.out": c.o1
"sen": tc.K
"rEtr": vo.P
"LoL.r": -260
"uPLi.r": 1360
This way the retransmission output limits will be 0 Volt for -260°C and 10Volt for +1360°C. This is corresponding to the measuring range of thermocouple K. If you want to change these limits , you may act on parameters "LoL.r" and "uPLi.r".
Do not forget to short-circuit pins 9 and 10 in order to enable the 0-10Volt output!
"c.out": c.o1
"sen": tc.K
"rEtr": vo.P
"LoL.r": -260
"uPLi.r": 1360
This way the retransmission output limits will be 0 Volt for -260°C and 10Volt for +1360°C. This is corresponding to the measuring range of thermocouple K. If you want to change these limits , you may act on parameters "LoL.r" and "uPLi.r".
Do not forget to short-circuit pins 9 and 10 in order to enable the 0-10Volt output!
-
- Posts: 36
- Joined: 09/02/2011, 14:33
- Location: Latvia
- Contact:
Re: [DRR245-ABC-T] as signal converter (TcK to 0-10Volt)
Is 4...20mA output passive or active from DRR245?
I want to connect it to PLC analog input.
Grazie!
I want to connect it to PLC analog input.
Grazie!
-
- Moderatore
- Posts: 1702
- Joined: 29/10/2010, 10:09
- Contact:
Re: [DRR245-ABC-T] as signal converter (TcK to 0-10Volt)
Is an active output.