[DRR245-ABC-T] as signal converter (TcK to 0-10Volt)

Post Reply
user54
Posts: 3
Joined: 10/12/2010, 13:53

[DRR245-ABC-T] as signal converter (TcK to 0-10Volt)

Post by user54 »

Which parameters should I set in order to use the unit as a SIGNAL CONVERTER (thermocouple K to 0-10Volt) :?:
Pixsys tecnico 1
Moderatore
Posts: 1702
Joined: 29/10/2010, 10:09
Contact:

Re: Controller DRR245

Post by Pixsys tecnico 1 »

For the requested application please set the following parameters as indicated :
"c.out": c.o1
"sen": tc.K
"rEtr": vo.P
"LoL.r": -260
"uPLi.r": 1360

This way the retransmission output limits will be 0 Volt for -260°C and 10Volt for +1360°C. This is corresponding to the measuring range of thermocouple K. If you want to change these limits , you may act on parameters "LoL.r" and "uPLi.r".

Do not forget to short-circuit pins 9 and 10 in order to enable the 0-10Volt output!
user497
Posts: 36
Joined: 09/02/2011, 14:33
Location: Latvia
Contact:

Re: [DRR245-ABC-T] as signal converter (TcK to 0-10Volt)

Post by user497 »

Is 4...20mA output passive or active from DRR245?

I want to connect it to PLC analog input.

Grazie!
Pixsys tecnico 1
Moderatore
Posts: 1702
Joined: 29/10/2010, 10:09
Contact:

Re: [DRR245-ABC-T] as signal converter (TcK to 0-10Volt)

Post by Pixsys tecnico 1 »

Is an active output.