Standard procedure to configure the correct sensor and avoid error E-5:
-Press FNC keyfor 3 seconds (SET key for ATR243-DRR245 series)
-Pressing arrow keys change the digit flashing, press SET key to pass to the next digit
-Enter the password "1234" ("123" for ATR121 series), press SET to confirm the last digit
-Scroll the parameters list using arrow Keys
-Go to the second parameter [SEN]
-Holding SET key, use arrows to scroll the sensors list
-Relase SET key when you see the correct sensor connected
-The confirmation of the configuration is made by pressing FNC key (both arrows key for ATR243-DRR245 series)
Now you will see on the display the correct temperature value.
HOW TO AVOID E-5 ERROR
-