Iris _

Pixsys Forum

everybody's effort for the same goal

Modbus/RTU polling data from PL260

Post Reply
user13099
Posts: 4
Joined: 30/03/2016, 2:24

Modbus/RTU polling data from PL260

Post by user13099 »

Hi,

I have a PL260 with a third party SCADA application running polling on the EXP1 port. Whenever I try to poll more than 20 registers the PLC does not respond healthily (4x0001 - 4x0020 works, 4x0001 - 4x0021 does not work - N.B. I'm not using VW0 aka 4x0000). I have tried 'Modbus Poll' as well and the same result occurs.

Is there a limitation for any reason, I didn't see anything in the user manual?

Regards
Pixsys tecnico 1
Moderatore
Posts: 1738
Joined: 29/10/2010, 10:09
Contact:

Re: Modbus/RTU polling data from PL260

Post by Pixsys tecnico 1 »

Hi,
you can do a multi-reading up to 16 consecutive words. Then you must send a new Modbus reading package
Post Reply