i have this error on display on power up , the T/C is ok (type K)..but i am usinga 10 meter compensating cable.. any ideas anyone??
						
									
						
										
							- 
			
					Pixsys tecnico 1
 - Moderatore
 - Posts: 1721
 - Joined: 29/10/2010, 10:09
 - Contact:
 
Re: i have error E-5 on display
What controller do you use?
Check the polarity of the thermocouple and the connections to the controllers. If the error doesn't disappear try to short-circuit the thermocouple input: you should see a temperature around 20°C.
						
									
						
										
							Check the polarity of the thermocouple and the connections to the controllers. If the error doesn't disappear try to short-circuit the thermocouple input: you should see a temperature around 20°C.
- 
			
					user967
 - Posts: 2
 - Joined: 21/04/2011, 16:41
 
Re: i have error E-5 on display
its a ATR121-AD controller..
first time we have used these..if i short the input its ok. any more ideas i can try?
						
									
						
										
							first time we have used these..if i short the input its ok. any more ideas i can try?
- 
			
					Pixsys tecnico 1
 - Moderatore
 - Posts: 1721
 - Joined: 29/10/2010, 10:09
 - Contact:
 
Re: i have error E-5 on display
It seems the thermocouple is badly connected or broken. Try to change it.