ATR244 wiring diagrams and configuration parameters for connection with 4..20mA EE210 probe

Post by user0020 »

Good morning,
i need to set up a system in which i would like to display the humidity and temperature with one of your EE210 probes.
I purchased an atr244-23bc-t regulator from one of your specialized distributors.
I want to connect a 4..20mA sensor, cod.2000.50.034 to the analog input of the atr244 temperature controller.
Could you tell me the electrical connections and configuration parameters for the required probe?
Thank you.
Pixsys tecnico 7
Moderatore
Posts: 95
Joined: 16/05/2024, 11:10

Re: ATR244 wiring diagrams and configuration parameters for connection with 4..20mA EE210 probe

Post by Pixsys tecnico 7 »

Good morning,
Below are the required probe or sensor connection diagrams for the atr244-23a-t and atr244-23bc-t models:
For humidity:

input / terminal 25 - "terminal 1 (V+)" EE210 sensor
input / terminal 28 - "terminal 2 (OUT1)" EE210 sensor
For temperature:
input / terminal 18 - "terminal 3 (OUT2)" EE210 sensor
And short-circuit terminals 14 and 17 for correct supply.

Subsequently, to log in and in order to modify the configuration parameters, proceed as follows:
press "FNC" for 3 seconds;
enter the password "1234";
press "FNC" again to confirm;
use the two arrows to scroll through the parameter groups;
press "SET" to allow modification of the selected parameter;
use the arrows to change its ownership;
press "SET" again to confirm the change;

Below are the parameters to modify to select the 4..20mA probe:
GROUP Parameters A - [A.in.1] - Analog input 1
Par. 1 [SEn.1] = 4-20
Par. 4 [L.L.i.1] = 0 ("value to associate with 4 mA" (with input 4..20 mA this parameter takes value associated to 4 mA))
Par. 5 [u.L.i.1] = 100 ("value to associate with 20 mA" (with input 4..20 mA this parameter takes value associated to 20 mA))

GROUP Parameters B - [A.in.2] - Analog input 2
Par. 18 [SEn.2] = 4-20
Par. 21 [L.L.i.2] = -20 ("value to associate with 4 mA" (with input 4..20 mA this parameter takes value associated to 4 mA))
Par. 22 [u.L.i.2] = 80 ("value to associate with 20 mA" (with input 4..20 mA this parameter takes value associated to 20 mA))

Press "FNC" once to return to parameter group selection,
Press "FNC" a second time to exit setup mode.


The value of the main setpoint (and alarm setpoint if enabled) can be modified from keyboard as follows:
Change the value on display 2 (bottom row) with up and down arrow keys;
(pressing the "set" key allows you to view the other setpoints, located on display 1 (top row). Display 2, on the other hand, indicates the setpoint type.
Change the digit on display 1 with up and down arrow keys.

To simplify the operation we suggest you to download "MyPixsys" APP which, via NFC communication, will allow to view and modify the setting parameters from your mobile phone or tablet.
MyPixsysApp: https://www.pixsys.net/software-e-soluzioni/mypixsysapp