Iris _

Pixsys Forum

everybody's effort for the same goal

ATR444 Using V+ Terminal to Provide Loop Power to Sensor

Post Reply
tomarra
Posts: 2
Joined: 19/07/2024, 23:22

ATR444 Using V+ Terminal to Provide Loop Power to Sensor

Post by tomarra »

Using the ATR444 for the first time, I can use a mA generator to supply process signal to AIN1 and my display scales accordingly based on my Lower Linear Value = 1.00 and Upper Linear Value = -1.00

4mA = 1.00
12mA = 0.00
20mA = -1.00

However, the actual sensor I need to wire to AIN requires 24VDC loop power.(P335 - Voltage Output is set for 24V.)

When I wire sensor between terminals 16 (AI1+) & 19 (V+) and short terminal 17 (A1-) & 20 (0V), my process reading remains at 1.00

However, when I place a mA meter in series, I do measure 12mA. Therefore, the display should indicate 0.00 for process.

I tried the same with a Fluke mA simulator and got the same result. Can the V+ terminal of the ATR444 not be used to power a sensor loop? Do I need an external 24V power supply?
Pixsys tecnico 1
Moderatore
Posts: 1738
Joined: 29/10/2010, 10:09
Contact:

Re: ATR444 Using V+ Terminal to Provide Loop Power to Sensor

Post by Pixsys tecnico 1 »

Hi,
if the sensor is a 2 wires power loop transducer, please use only PIN 19 (+V, power to the sensor) and PIN 16 (AI+, output of the sensor) without shorting terminals 17 (A1-) & 20 (0V).
tomarra
Posts: 2
Joined: 19/07/2024, 23:22

Re: ATR444 Using V+ Terminal to Provide Loop Power to Sensor

Post by tomarra »

That worked! Thank you!
Post Reply