Iris _

Pixsys Forum

everybody's effort for the same goal

ATR144-ABC connection and parameterization with Tc-j thermocouple

Post Reply
user0020
Posts: 47
Joined: 16/05/2024, 9:39

ATR144-ABC connection and parameterization with Tc-j thermocouple

Post by user0020 »

Good morning,
I purchased an atr144-abc thermoregulator.
I would like to connect a thermocouple temperature sensor to the analog input of the controller.
The model is type j.
Could you tell me the connections and parameters to enter?
Thank you.
Pixsys tecnico 7
Moderatore
Posts: 134
Joined: 16/05/2024, 11:10

Re: ATR144-ABC connection and parameterization with Tc-j thermocouple

Post by Pixsys tecnico 7 »

Good morning,
Below are the connection diagrams of the required probe or sensor:
Model atr144-abc
input / terminal 11 - blue wire "-" tcj probe
input / terminal 12 - red wire "+" tcj probe
For any extensions, use compensated cable and clamps suitable for the
thermocouple used (compensated).

Subsequently, to log in and in order to modify the configuration parameters, proceed as follows:
press "FNC" for 3 seconds;
enter the password "1234";
press "FNC" again to confirm;
use the two arrows to scroll through the parameter groups;
press "SET" to allow modification of the selected parameter;
use the arrows to change its ownership;
press "SET" again to confirm the change;

Below are the parameters to modify to select the tc-j probe:
GROUP Parameters A - [A.in.1] - Analog input 1
Par. 1 [SEn.1] = tc. j

Press "FNC" once to return to parameter group selection,
Press "FNC" a second time to exit setup mode.


The value of the main setpoint (and alarm setpoint if enabled) can be modified from keyboard as follows:
Change the value on display 2 (bottom row) with up and down arrow keys;
(pressing the "set" key allows you to view the other setpoints, located on display 1 (top row). Display 2, on the other hand, indicates the setpoint type.
Change the digit on display 1 with up and down arrow keys.

To simplify the operation we suggest you to download "MyPixsys" APP which, via NFC communication, will allow to view and modify the setting parameters from your mobile phone or tablet.
MyPixsysApp: https://www.pixsys.net/software-e-soluzioni/mypixsysapp
Post Reply