Post by user898 »

I am facing an issue with PL110 that causes it to reset with random intervals. What are potential reasons for this type of behavior?
Pixsys tecnico 1
Moderatore
Posts: 1735
Joined: 29/10/2010, 10:09
Contact:

Re: PL110 software reset

Post by Pixsys tecnico 1 »

Are you using interrupt?
Are you usin C code?
Can you attach you PLC software?
user898
Posts: 4
Joined: 10/04/2011, 8:41

Re: PL110 software reset

Post by user898 »

Thank you for the reply. Interrupt (100ms) with software PID update is in use and it seems that problems relate to this combo. I couldn't attach the the full code put it seems this single line (on 100ms interrupt) causes the problem.
pid_100ms.png
You do not have the required permissions to view the files attached to this post.
Pixsys tecnico 1
Moderatore
Posts: 1735
Joined: 29/10/2010, 10:09
Contact:

Re: PL110 software reset

Post by Pixsys tecnico 1 »

Ok,
please try this:
eliminate this line on the interrupt, and put the same line in the main code, using a timer to "scan" the code every 100mS.