Iris _

Pixsys Forum

everybody's effort for the same goal

atr142 4-20ma

Post Reply
gulzar
Posts: 5
Joined: 24/01/2020, 11:39

atr142 4-20ma

Post by gulzar »

Hello
I need to connect the hs-4200205408 to atr142, on this i used the option 4-20mA, but there is issue with option, it doesent work(e-5 err). How to connect it correcly ?
Pixsys tecnico 6
Moderatore
Posts: 1208
Joined: 12/09/2016, 14:49

Re: atr142 4-20ma

Post by Pixsys tecnico 6 »

Good morning,
what supply voltage does your 4-20mA sensor require?

Best regards.
gulzar
Posts: 5
Joined: 24/01/2020, 11:39

Re: atr142 4-20ma

Post by gulzar »

15-30 VDC
Pixsys tecnico 6
Moderatore
Posts: 1208
Joined: 12/09/2016, 14:49

Re: atr142 4-20ma

Post by Pixsys tecnico 6 »

What's the power supply to the ATR144?
gulzar
Posts: 5
Joined: 24/01/2020, 11:39

Re: atr142 4-20ma

Post by gulzar »

Pixsys tecnico 6 wrote:What's the power supply to the ATR144?
24 vdc
Pixsys tecnico 6
Moderatore
Posts: 1208
Joined: 12/09/2016, 14:49

Re: atr142 4-20ma

Post by Pixsys tecnico 6 »

Good morning,
The maximum voltage the ATR142 provides to power a 4-20mA sensor is 12V. Your sensor requires a minimum power supply of 15Vdc, so you must use the 24Vdc transformer power supply.
Connect the transformer's V+ to the sensor's power supply, then connect the sensor's output to the ATR142's PIN 12 and then connect the ATR144's PIN 11 to the V- of its 24Vdc power supply.

Best Regards.
gulzar
Posts: 5
Joined: 24/01/2020, 11:39

Re: atr142 4-20ma

Post by gulzar »

Thanks, it helped! How can I do that this number is not a whole number, but for example 2.5 ?
Pixsys tecnico 6
Moderatore
Posts: 1208
Joined: 12/09/2016, 14:49

Re: atr142 4-20ma

Post by Pixsys tecnico 6 »

Good morning,
if you need enable a decimal point, you can use the parameter number 3.[d.P]="0.0".

Best Regards.
gulzar
Posts: 5
Joined: 24/01/2020, 11:39

Re: atr142 4-20ma

Post by gulzar »

Pixsys tecnico 6 wrote:Good morning,
if you need enable a decimal point, you can use the parameter number 3.[d.P]="0.0".

Best Regards.
Yes, I have already tried to change this setting, then it shows me not 2, but 0,2.

along with this parameter it was also necessary to change 7 uP.L.i. - Upper Linear Input.
Thanks for the help!
Pixsys tecnico 6
Moderatore
Posts: 1208
Joined: 12/09/2016, 14:49

Re: atr142 4-20ma

Post by Pixsys tecnico 6 »

Yes, It is correct. Thanks for your feedback.

Best Regards.
Post Reply