entrada analógica 4-20mA en PL260
-
- Posts: 1
- Joined: 10/10/2017, 13:28
entrada analógica 4-20mA en PL260
Hello, I would like to know how to configure the analog inputs of 0-20mA in the PL260
-
- Moderatore
- Posts: 1201
- Joined: 12/09/2016, 14:49
Re: entrada analógica 4-20mA en PL260
Hi,
follow this dip-switch settings example to enable the mA AI1 input.
DIP1=ON
DIP2=OFF
DIP3=OFF
DIP4=OFF
Special marker value:
Set the SM40 = 5 (enable 0-20mA signal) and you can define the signal range using the SM46 and SM52.
Best Regards.
follow this dip-switch settings example to enable the mA AI1 input.
DIP1=ON
DIP2=OFF
DIP3=OFF
DIP4=OFF
Special marker value:
Set the SM40 = 5 (enable 0-20mA signal) and you can define the signal range using the SM46 and SM52.
Best Regards.