Hello,
1)
I have ATR243-31ABC and I cannot find an option that is mentioned in page 20. ->''SScY'' (soft start cycle)
In parameter 59 "Operating mode" there is no such option.
2)
I attached necessary task I have to make, does soft start in cooling mode would work?
Thanks!
[ATR243] Gradient and soft start in cooling
-
- Posts: 19
- Joined: 25/02/2014, 13:37
[ATR243] Gradient and soft start in cooling
You do not have the required permissions to view the files attached to this post.
-
- Moderatore
- Posts: 1702
- Joined: 29/10/2010, 10:09
- Contact:
Re: Gradient and soft start
What's the firmware version of the regulator? You can see it during boot of hte regulator. It is something like 1.22
-
- Posts: 19
- Joined: 25/02/2014, 13:37
Re: Gradient and soft start
Yes, it is 1.22
I now set parameters
1) Action type = cooling
2) gradient = 60
3) Hysteresis = 0.5 C
It seem like everything is working, not sure about precision yet
I now set parameters
1) Action type = cooling
2) gradient = 60
3) Hysteresis = 0.5 C
It seem like everything is working, not sure about precision yet
-
- Moderatore
- Posts: 1702
- Joined: 29/10/2010, 10:09
- Contact:
Re: Gradient and soft start
Hi,
''SScY'' mode is only avaiable from firmware versione 1.27.
''SScY'' mode is only avaiable from firmware versione 1.27.