[ATR142] Control heating process in PID with SSR output
-
user497
- Posts: 36
- Joined: 09/02/2011, 14:33
- Location: Latvia
- Contact:
[ATR142] Control heating process in PID with SSR output
Hello,
we have ATR142, that we use with PID to control heating process with SSR output.
But we have problem, that all the time controller is holding higher temperature as in setpoint.
If setpoint is 37, it is holding 40...42C.
We did already a lot of Autotune, but no results.
Parameters:
18 Pb = 7
19 ti = 999,9 !!!!!!! (MAX number in this parameter
20 td = 249,9 !!!!!!! ( And this looks like 1/4 from ti parameter )
IT looks very strange, that it is taking so big numbers in 19. and 20. parameter!
Where can we look for some problem? What is it indicating with 999 and 249,99 ???
And does in this case parameter 21. tc (Cycle time) take some effect on PID?
we have ATR142, that we use with PID to control heating process with SSR output.
But we have problem, that all the time controller is holding higher temperature as in setpoint.
If setpoint is 37, it is holding 40...42C.
We did already a lot of Autotune, but no results.
Parameters:
18 Pb = 7
19 ti = 999,9 !!!!!!! (MAX number in this parameter
20 td = 249,9 !!!!!!! ( And this looks like 1/4 from ti parameter )
IT looks very strange, that it is taking so big numbers in 19. and 20. parameter!
Where can we look for some problem? What is it indicating with 999 and 249,99 ???
And does in this case parameter 21. tc (Cycle time) take some effect on PID?
You do not have the required permissions to view the files attached to this post.
-
Pixsys tecnico 1
- Moderatore
- Posts: 1737
- Joined: 29/10/2010, 10:09
- Contact:
Re: [ATR142] Control heating process in PID with SSR output
Hi, [T.c.] parameter is very important in PID action because is the cycle time of the output. In your case, using SSR as output, you have to set it as 1 Second. Then try to relaunch the auto-tune function (@ about 20°C if you work around 37°)
-
user497
- Posts: 36
- Joined: 09/02/2011, 14:33
- Location: Latvia
- Contact:
Re: [ATR142] Control heating process in PID with SSR output
Hello,
we still have some problems, that it is going over the setpoint for some 3...4C .
After Auto tune the parameters are like this:
Pb= 8;
Ti= 100;
td= 251
tc=1
What can we try to change, to have smaller overheat? ( ~ 0,5C is the best!!)
Thank YOu
we still have some problems, that it is going over the setpoint for some 3...4C .
After Auto tune the parameters are like this:
Pb= 8;
Ti= 100;
td= 251
tc=1
What can we try to change, to have smaller overheat? ( ~ 0,5C is the best!!)
Thank YOu
-
Pixsys tecnico 1
- Moderatore
- Posts: 1737
- Joined: 29/10/2010, 10:09
- Contact:
Re: [ATR142] Control heating process in PID with SSR output
Hi, Td value is very strange, try to set it as "25" (normally is 1/4 of Ti).
-
user497
- Posts: 36
- Joined: 09/02/2011, 14:33
- Location: Latvia
- Contact:
Re: [ATR142] Control heating process in PID with SSR output
Hello ,
thank You!
I changed this value to 25, but still, it is going over the set point! (Set point was 25C, and the highest was 29,2 C ).
The problem is, that the heating element is very small ~ 120W.
Which parameter can we change, to decrease overshoot?
thank You!
I changed this value to 25, but still, it is going over the set point! (Set point was 25C, and the highest was 29,2 C ).
The problem is, that the heating element is very small ~ 120W.
Which parameter can we change, to decrease overshoot?
-
Pixsys tecnico 1
- Moderatore
- Posts: 1737
- Joined: 29/10/2010, 10:09
- Contact:
Re: [ATR142] Control heating process in PID with SSR output
Temperature is stabilized 4-5°C over the setpoint or goes up and down?
-
user497
- Posts: 36
- Joined: 09/02/2011, 14:33
- Location: Latvia
- Contact:
Re: [ATR142] Control heating process in PID with SSR output
It goes up 4-5C over setpoint and then slowly comes back to setpoint, as You can see in attached file some posts back!
-
Pixsys tecnico 1
- Moderatore
- Posts: 1737
- Joined: 29/10/2010, 10:09
- Contact:
Re: [ATR142] Control heating process in PID with SSR output
Increase "Ti" to 125, "Td" to 1/4 of "Ti". Try to limit the power output with p.22 [o.po.L.] to 80-90%.
If it doesn't work:
c.HY 0.0 (if it is different)
Pb 12
Ti 600
Td 150
o.po.L. 100
Wait 2 hours (recording the process) and post the results.
If it doesn't work:
c.HY 0.0 (if it is different)
Pb 12
Ti 600
Td 150
o.po.L. 100
Wait 2 hours (recording the process) and post the results.
-
user497
- Posts: 36
- Joined: 09/02/2011, 14:33
- Location: Latvia
- Contact:
Re: [ATR142] Control heating process in PID with SSR output
Hello,
i still have no changes in PID. I did autotune one more time and again the same!
I seted up also:
12
600
150
but the result was the same, some 5 degree ofer setpoint.
Maybe the problem is that, the heater is with very big inertia?
Because after autotune it used:
Pb=6
Ti=850
Td=215
And how can it know after autotune, what is important for us: time-speed ( to reach 98% of setpoint) or overshoot, what he can allow?
Because of cours, if the time is more important it will give more overshoot. But in our case the time is not important, but overshoot is more important!
P.S.
I`m using ATR121-B ( i choosed this topic, because there was PID controll already)
i still have no changes in PID. I did autotune one more time and again the same!
I seted up also:
12
600
150
but the result was the same, some 5 degree ofer setpoint.
Maybe the problem is that, the heater is with very big inertia?
Because after autotune it used:
Pb=6
Ti=850
Td=215
And how can it know after autotune, what is important for us: time-speed ( to reach 98% of setpoint) or overshoot, what he can allow?
Because of cours, if the time is more important it will give more overshoot. But in our case the time is not important, but overshoot is more important!
P.S.
I`m using ATR121-B ( i choosed this topic, because there was PID controll already)
-
Pixsys tecnico 1
- Moderatore
- Posts: 1737
- Joined: 29/10/2010, 10:09
- Contact:
Re: [ATR142] Control heating process in PID with SSR output
Remember to disable [TunE] parameter before set manually PID parameters. PID parameters calculated (12/850/215) are correct but your problem is that the process is very slow (overshoot came when temperature reach the setpoint and also after 1-2 hours). Disable autotuning, set PID parameters as I said (12/850/215) and wait 2 hours recording the data. Then post me the recorded graphic.
-
user497
- Posts: 36
- Joined: 09/02/2011, 14:33
- Location: Latvia
- Contact:
Re: [ATR142] Control heating process in PID with SSR output
Hello,
so, i made a test:
Pb=12
TI=600
Td=150
Tune: disabled
But the same problem.
In data, temperature are little bit higher, because it is closer to heater.
But the same problem with overheat!!!
The red dot line is alarm temperature : + 38C ( + 37,5 + 0,5 C ).
P.S.
We use ATR121-B
so, i made a test:
Pb=12
TI=600
Td=150
Tune: disabled
But the same problem.
In data, temperature are little bit higher, because it is closer to heater.
But the same problem with overheat!!!
The red dot line is alarm temperature : + 38C ( + 37,5 + 0,5 C ).
P.S.
We use ATR121-B
You do not have the required permissions to view the files attached to this post.
-
Pixsys tecnico 1
- Moderatore
- Posts: 1737
- Joined: 29/10/2010, 10:09
- Contact:
Re: [ATR142] Control heating process in PID with SSR output
Ok, so set:
Pb: 15
Ti: 800
Td: 200
rEg: H.o.o.
Pb: 15
Ti: 800
Td: 200
rEg: H.o.o.
-
user497
- Posts: 36
- Joined: 09/02/2011, 14:33
- Location: Latvia
- Contact:
Re: [ATR142] Control heating process in PID with SSR output
Here it is!
Not 2 hours, because it was already working day evening, but still overshoot is to big, over 40C.
Is there some more options to do?
Not 2 hours, because it was already working day evening, but still overshoot is to big, over 40C.
Is there some more options to do?
You do not have the required permissions to view the files attached to this post.
-
Pixsys tecnico 1
- Moderatore
- Posts: 1737
- Joined: 29/10/2010, 10:09
- Contact:
Re: [ATR142] Control heating process in PID with SSR output
With ATR121 we are so limitating in PID parameters so try:
Pb: 20
Ti: 999
Td: 500
rEg: H.o.o.
The first overshoot there will still be, but after that it would be more stable.
Pb: 20
Ti: 999
Td: 500
rEg: H.o.o.
The first overshoot there will still be, but after that it would be more stable.
-
user497
- Posts: 36
- Joined: 09/02/2011, 14:33
- Location: Latvia
- Contact:
Re: [ATR142] Control heating process in PID with SSR output
Hello, thank You, i will try this on next working day.
But is it possible to do with ATR142?
I can still change it, because in this case it is more important to disable that overshoot!
Thank You.
But is it possible to do with ATR142?
I can still change it, because in this case it is more important to disable that overshoot!
Thank You.
-
Pixsys tecnico 1
- Moderatore
- Posts: 1737
- Joined: 29/10/2010, 10:09
- Contact:
Re: [ATR142] Control heating process in PID with SSR output
With ATR142 we can use softstart to avoid overshoot when reaching the sepoint
-
user497
- Posts: 36
- Joined: 09/02/2011, 14:33
- Location: Latvia
- Contact:
Re: [ATR142] Control heating process in PID with SSR output
Hello,
so i tested it and now it is better, but still just little bit to high (max was ~ 38C, Setpoint: 37.0) (The red dot line is alarm line( 38C) - in attachment)
we need just a little bit less : max 37,5.
Can i try to change something more: bigger td ????
For information:
And in ATR142 case i need to change output power limit? or other parameter?
so i tested it and now it is better, but still just little bit to high (max was ~ 38C, Setpoint: 37.0) (The red dot line is alarm line( 38C) - in attachment)
we need just a little bit less : max 37,5.
Can i try to change something more: bigger td ????
For information:
And in ATR142 case i need to change output power limit? or other parameter?
You do not have the required permissions to view the files attached to this post.
-
Pixsys tecnico 1
- Moderatore
- Posts: 1737
- Joined: 29/10/2010, 10:09
- Contact:
Re: [ATR142] Control heating process in PID with SSR output
With ATR142 you will use 51 [GrAd] parameter to reach the setpoint slowly.
Now, with ATR121 you can try to increase Pb to 25 and Td to 600.
Now, with ATR121 you can try to increase Pb to 25 and Td to 600.
-
user497
- Posts: 36
- Joined: 09/02/2011, 14:33
- Location: Latvia
- Contact:
Re: [ATR142] Control heating process in PID with SSR output
Hello, so i changed controller to ATR142-ABC
Reg = Ho.o
Pb = 25
Ti = 999.9
Td = 600
tc = 1.0
tune = disabled
oPNo = PrcY
Grad: 10.0
Now its almost good, but still as You can see in graph, it is with bigger overshoot as it must be!
Setpoint: 37C ( +- 0,5C ) , but here max is 38C!
Is there some other parameter, which we can change?
Reg = Ho.o
Pb = 25
Ti = 999.9
Td = 600
tc = 1.0
tune = disabled
oPNo = PrcY
Grad: 10.0
Now its almost good, but still as You can see in graph, it is with bigger overshoot as it must be!
Setpoint: 37C ( +- 0,5C ) , but here max is 38C!
Is there some other parameter, which we can change?
You do not have the required permissions to view the files attached to this post.
-
Pixsys tecnico 1
- Moderatore
- Posts: 1737
- Joined: 29/10/2010, 10:09
- Contact:
Re: [ATR142] Control heating process in PID with SSR output
Try limit the output power to 80% with parameter P22 [o.Po.L] as "80".
You have to leave [oPNo] = "cont" if you use only [Grad] parameter (we are not using pre-programmed cycle but only a fixed gradient to reach the setpoint).
You have to leave [oPNo] = "cont" if you use only [Grad] parameter (we are not using pre-programmed cycle but only a fixed gradient to reach the setpoint).