I need help to setup this unit to control pressure manualy in selected steps.
Pressure sensor O/P = 0-10v (-20 to 20 kpa)
controler output = 0-10v (-20 to 20 kpa) linear EDITED
Please advice what settings I need to change, so that I can dial up
a pressure value that I need controlled.
Display to show kpa value.
[ATR243-20ABC] 0-10V "inverse" retransmission parameters
-
- Posts: 3
- Joined: 27/11/2012, 2:14
[ATR243-20ABC] 0-10V "inverse" retransmission parameters
Last edited by user4432 on 27/11/2012, 23:00, edited 2 times in total.
-
- Moderatore
- Posts: 1678
- Joined: 29/10/2010, 10:09
- Contact:
Re: ATR243-20ABCF , 0-10v setup
Hi,
so you have an input signal (pressure) 0-10V from -20 to +20kPa and you need an output signal 0-10V to control this pressure (at a specified setpoint) or to retransmit this pressure proportionally (input -20kPa..+20kPa is equal output 0V..10V)?
so you have an input signal (pressure) 0-10V from -20 to +20kPa and you need an output signal 0-10V to control this pressure (at a specified setpoint) or to retransmit this pressure proportionally (input -20kPa..+20kPa is equal output 0V..10V)?
-
- Posts: 3
- Joined: 27/11/2012, 2:14
Re: ATR243-20ABCF , 0-10v setup
I want to retransmit this pressure proportionally (input -20kPa..+20kPa is equal output 0V..10V)? and scale voltages to kpa.
The output is INVERSE and switching :: > setpoint = 0v
:: < setpoint = 10v
my setup is
1 cout = c. O1
2 Sen = 010
4 Lols = -20
5 upls = 20
6 Lo.li = -20
7 up.li = 200
18, 19 & 20 = 0.0
67 = uo.c
68 = -20.0
69 = 20.0
Your assistance is needed
The output is INVERSE and switching :: > setpoint = 0v
:: < setpoint = 10v
my setup is
1 cout = c. O1
2 Sen = 010
4 Lols = -20
5 upls = 20
6 Lo.li = -20
7 up.li = 200
18, 19 & 20 = 0.0
67 = uo.c
68 = -20.0
69 = 20.0
Your assistance is needed
-
- Moderatore
- Posts: 1678
- Joined: 29/10/2010, 10:09
- Contact:
Re: ATR243-20ABCF , 0-10v setup
If you want to retransmit "input to output switched" you need to configure ATR243:
C.out : c0.1
Sen: 0.10
LoLi: -20
uPLi: 20
retr: uo.P
LoLr: +20
uPLr: -20
Before this, reset the controller to the default configuration entering "9999" as the setup password.
C.out : c0.1
Sen: 0.10
LoLi: -20
uPLi: 20
retr: uo.P
LoLr: +20
uPLr: -20
Before this, reset the controller to the default configuration entering "9999" as the setup password.
-
- Posts: 3
- Joined: 27/11/2012, 2:14
Re: ATR243-20ABCF , 0-10v setup
All good now
C.out was set wrongly.
C.out was set wrongly.