[ATR142-ABC] Output relay after pre-programmed cycle ends

Posted: 16/03/2011, 10:06
by user497
Buongiorno!

Is there a controller from Pixsys, which can give a output signal, after the holding time ends? ( i mean pre-programmed cycle - i need output signal, when the time is over! )
Thank You in advance!

Re: Output related to the difference between AI1 and AI2

Posted: 16/03/2011, 12:09
by Pixsys tecnico 1
Hi,
if you need to close a contact after a certain time (without monitoring any temperature), you can simply use a TCT101-1ABC or a ATR142 in timer-mode.
For more information visit our website to visualize the relative manuals.

Re: Output related to the difference between AI1 and AI2

Posted: 17/03/2011, 15:07
by user497
Hello,

i need that output, after pre-programmed cycle ends! When controller reach the set point, it hold that temperature for holding time, that is already in controller, but after that holding time ends, we need other output signal, that process is ready!

Thank You!

Re: Output related to the difference between AI1 and AI2

Posted: 21/03/2011, 9:51
by Pixsys tecnico 1
You can use an ATR142-ABC in "pre-programmed cycle" mode and set:

[AL.1]: "St.AL"
[A1.S.o]: "nc.S"

In this way the Q2 relay closes when the cycle ends or it is in stop.

Re: Output related to the difference between AI1 and AI2

Posted: 21/03/2011, 10:00
by user497
Thank You!

I will test it! But i think, it will be ok!