[TD240] Probleme connection PlProg

Posted: 27/11/2012, 11:12
by user2909
bonjour tous le monde
j'ai un probleme de connection de l'ordinateur et le plc TD 240

jai attache image de message d'erreur

voulez vous bien me guider a me connecter

NB: je suis nouveau dans le materiels pixsys

merci beaucoup

Re: Probleme connection with TD 240

Posted: 27/11/2012, 14:20
by Pixsys tecnico 1
Hi,
PlProg doesn't recognize the PLC connect to the port com16. This error can caused because you have LabSoftView open with the memory card connect to the PC. Try to open only PlProg and connect only the TD240 to the pc; then re-click to the first line of the program line ("plc on COM16 PC).

Re: Probleme connection with TD 240

Posted: 14/01/2016, 13:18
by user10989
Pixsys tecnico 1 wrote:Hi,
PlProg doesn't recognize the PLC connect to the port com16. This error can caused because you have LabSoftView open with the memory card connect to the PC. Try to open only PlProg and connect only the TD240 to the pc; then re-click to the first line of the program line ("plc on COM16 PC).

Hello,

I have a same problem with PlProg. I can not send program to PLC, but i have not LabSoftView. TD240-AD is connect to PC.
Help please

Re: [TD240] Probleme connection PlProg

Posted: 14/01/2016, 14:21
by Pixsys tecnico 1
Hi,
are you using some serial converter USB-RSR232 or are you connecting directly from PC-DB8 RSR232 to the TD240?
Is the first time you try to connect with this PC to this TD240?

Re: [TD240] Probleme connection PlProg

Posted: 14/01/2016, 14:46
by user10989
Pixsys tecnico 1 wrote:Hi,
are you using some serial converter USB-RSR232 or are you connecting directly from PC-DB8 RSR232 to the TD240?
Is the first time you try to connect with this PC to this TD240?
NO,i am using serial converter USB-RS485 with conector DB9. It is not first time.I was send program to PLC three times and it works, but now i cant send.

Re: [TD240] Probleme connection PlProg

Posted: 14/01/2016, 15:41
by Pixsys tecnico 1
Try to connect to TD240 by clicking 1 time to:
1.png
.

Try to download program by using the function "PLC / PLC Maintenance / Update PLC firmware":
-Power-off TD240
-launch PLC update and during connection progress power-on TD240

Re: [TD240] Probleme connection PlProg

Posted: 18/01/2016, 10:00
by user10989
Pixsys tecnico 1 wrote:Try to connect to TD240 by clicking 1 time to:
1.png
.

Try to download program by using the function "PLC / PLC Maintenance / Update PLC firmware":
-Power-off TD240
-launch PLC update and during connection progress power-on TD240
I can not resolve problem in this way. How i can restore TD240 on default ?

Re: [TD240] Probleme connection PlProg

Posted: 18/01/2016, 10:14
by Pixsys tecnico 1
The procedure I describe is used to restore TD240.

I suggest you to connect using standard RS232 to COM2 (on DB9 or DB25, default serial port for programming).

Re: [TD240] Probleme connection PlProg

Posted: 21/01/2016, 11:27
by user10989
Pixsys tecnico 1 wrote:The procedure I describe is used to restore TD240.

I suggest you to connect using standard RS232 to COM2 (on DB9 or DB25, default serial port for programming).
Thank you