[ATR401] READ IF HEATER IS WORKING

Posted: 02/08/2012, 10:13
by user2366
hello
i want to read out if the heater is working or not. i use an atr401-22abc-t.
heating is on relay output q1 (3,5)
therfore i use relay output q2 (6,8) which is supplied with 4,7V.
to get an output i set
37 [AL.1] to St.Al
38 [A.1.Pr] to Pro1
39 [A.1.S.o.] to n.o. start
but nothing happens...
i thought when the heater is in progress i get a signal, if its not heating no signal...
do you have any idea what i did wrong?
thx
ug

Re: READ IF HEATER IS WORKING - atr401-22abc-t

Posted: 02/08/2012, 14:27
by Giulio Buffa
Hallo
It is not possible to program an Alarm relay in this way.
If you nead to duplicate the main output, add an external relay/contactor (with 2 contact output) and link your services like necessary.