Good morning,
I purchased a drr244-13abc regulator.
I want to connect a thermocouple probe or sensor to the AI1 probe input.
I have a type K thermocouple model with 2 wires, one green and the other red.
How can I connect it to the terminals and which are the parameters i should enter?
Thank you.
DRR244-13ABC connection with tc-K probe
-
Pixsys tecnico 7
- Moderatore
- Posts: 132
- Joined: 16/05/2024, 11:10
Re: DRR244-13ABC connection with tc-K probe
Good morning,
Below are the connection diagrams of the required probe or sensor:
input / terminal 13 - red wire "+"
input / terminal 14 - green wire "-"
For any extensions, use compensated cable and clamps suitable for the
thermocouple used (compensated).
Subsequently, to log in and in order to modify the configuration parameters, proceed as follows:
press "FNC" for 3 seconds;
enter the password "1234";
press "FNC" again to confirm;
use the two arrows to scroll through the parameter groups;
press "SET" to allow modification of the selected parameter;
use the arrows to change its ownership;
press "SET" again to confirm the change;
Below are the configuration parameters to modify to select the required probe:
GROUP Parameters A - [A.in.1] - Analog input 1
Par. 1 [SEn.1] = tc. k
Press "FNC" once to return to parameter group selection,
Press "FNC" a second time to exit setup mode.
The value of the main setpoint (and alarm setpoint if enabled) can be modified from keyboard as follows:
Change the value on display 2 (bottom row) with up and down arrow keys;
(pressing the "set" key allows you to view the other setpoints, located on display 1 (top row). Display 2, on the other hand, indicates the setpoint type.
Change the digit on display 1 with up and down arrow keys.
To simplify the operation we suggest you to download "MyPixsys" APP which, via NFC communication, will allow to view and modify the setting parameters from your mobile phone or tablet.
MyPixsysApp: https://www.pixsys.net/software-e-soluzioni/mypixsysapp
Below are the connection diagrams of the required probe or sensor:
input / terminal 13 - red wire "+"
input / terminal 14 - green wire "-"
For any extensions, use compensated cable and clamps suitable for the
thermocouple used (compensated).
Subsequently, to log in and in order to modify the configuration parameters, proceed as follows:
press "FNC" for 3 seconds;
enter the password "1234";
press "FNC" again to confirm;
use the two arrows to scroll through the parameter groups;
press "SET" to allow modification of the selected parameter;
use the arrows to change its ownership;
press "SET" again to confirm the change;
Below are the configuration parameters to modify to select the required probe:
GROUP Parameters A - [A.in.1] - Analog input 1
Par. 1 [SEn.1] = tc. k
Press "FNC" once to return to parameter group selection,
Press "FNC" a second time to exit setup mode.
The value of the main setpoint (and alarm setpoint if enabled) can be modified from keyboard as follows:
Change the value on display 2 (bottom row) with up and down arrow keys;
(pressing the "set" key allows you to view the other setpoints, located on display 1 (top row). Display 2, on the other hand, indicates the setpoint type.
Change the digit on display 1 with up and down arrow keys.
To simplify the operation we suggest you to download "MyPixsys" APP which, via NFC communication, will allow to view and modify the setting parameters from your mobile phone or tablet.
MyPixsysApp: https://www.pixsys.net/software-e-soluzioni/mypixsysapp