Good morning,
thank you for your request, the device indicated is a regulator with different options, defined by the alphanumeric code following the prefix "ATR244".
Below are the connection diagrams of the probe or sensor required based on the model of its thermoregulator:
Model ATR244-12ABC and ATR244-13ABC
input / terminal 19 - red wire "+" tck probe
input / terminal 18 - green wire "-" tck probe
For any extensions, use compensated cable and clamps suitable for the
thermocouple used (compensated).
Model ATR244-23x
input / terminal 28 - red wire "+" tck probe
input / terminal 27 - green wire "-" tck probe
P.S.: this model also accepts a second tck probe which can be connected to terminals 18 and 17
Subsequently, to log in and in order to modify the configuration parameters, proceed as follows:
press "FNC" for 3 seconds;
enter the password "1234";
press "FNC" again to confirm;
use the two arrows to scroll through the parameter groups;
press "SET" to allow modification of the selected parameter;
use the arrows to change its ownership;
press "SET" again to confirm the change;
Below are the parameters to be modified to select the thermocouple probe k:
GROUP Parameters A - [A.in.1] - Analog input 1
Par. 1 [SEn.1] = tc. k
Press "FNC" once to return to parameter group selection,
Press "FNC" a second time to exit setup mode.
The value of the main setpoint (and alarm setpoint if enabled) can be modified from keyboard as follows:
Change the value on display 2 (bottom row) with up and down arrow keys;
(pressing the "set" key allows you to view the other setpoints, located on display 1 (top row). Display 2, on the other hand, indicates the setpoint type.
Change the digit on display 1 with up and down arrow keys.
To simplify the operation we suggest you to download "MyPixsys" APP which, via NFC communication, will allow to view and modify the setting parameters from your mobile phone or tablet.
MyPixsysApp:
https://www.pixsys.net/software-e-soluzioni/mypixsysapp