Good morning,
thank you for your request, the device indicated is a regulator with different options, defined by the alphanumeric code following the prefix "ATR244".
Below are the connection diagrams of the probe or sensor required based on the model of its thermoregulator:
Model ATR244-12ABC and ATR244-13ABC
input / terminal 19 - pt100 probe red wire
input / terminal 18 - white wire PT100 probe
input / terminal 17 - pt100 probe red wire
Model ATR244-23x
input / terminal 28 - pt100 probe red wire
input / terminal 27 - white wire PT100 probe
input / terminal 26 - pt100 probe red wire
P.S.: this model also accepts a second probe which can be connected to terminals 16, 17, 18
Subsequently, to log in and in order to modify the configuration parameters, proceed as follows:
press "FNC" for 3 seconds;
enter the password "1234";
press "FNC" again to confirm;
use the two arrows to scroll through the parameter groups;
press "SET" to allow modification of the selected parameter;
use the arrows to change its ownership;
press "SET" again to confirm the change;
Below are the parameters to modify to select the 3-wire PT100 probe:
GROUP Parameters A - [A.in.1] - Analog input 1
Par. 1 [SEn.1] = Pt100
Press "FNC" once to return to parameter group selection,
Press "FNC" a second time to exit setup mode.
The value of the main setpoint (and alarm setpoint if enabled) can be modified from keyboard as follows:
Change the value on display 2 (bottom row) with up and down arrow keys;
Pressing the "set" key allows you to view the other setpoints, located on display 1 (top row). Display 2, on the other hand, indicates the setpoint type.
Change the digit on display 1 with up and down arrow keys.