Iris _

Pixsys Forum

everybody's effort for the same goal

ATR144-ABC-T master serial port section missing

Post Reply
Halsteads
Posts: 14
Joined: 30/04/2022, 16:49

ATR144-ABC-T master serial port section missing

Post by Halsteads »

ATR144 User Manual, Table of Configuration Parameters, (p74), section 12.I refers to GROUP L – Master Serial Port (only available on ATR144-ABC-T).

Using ATR144 front panel keyboard GROUP L is missing, or hidden? (Groups E and G are also missing). Is there a way to access this without using the Windows software?

Will try using My Pixsys app when I can get it to work.


Screenshot 2024-04-07 at 17.37.55.png
You do not have the required permissions to view the files attached to this post.
Pixsys tecnico 1
Moderatore
Posts: 1736
Joined: 29/10/2010, 10:09
Contact:

Re: ATR144-ABC-T master serial port section missing

Post by Pixsys tecnico 1 »

Hi,
can you tell us the firmware version of the controller?
You can see it during the powering of the controller, it is like "1.05"
Halsteads
Posts: 14
Joined: 30/04/2022, 16:49

Re: ATR144-ABC-T master serial port section missing

Post by Halsteads »

thanks,

firmware is 1.04
Pixsys tecnico 1
Moderatore
Posts: 1736
Joined: 29/10/2010, 10:09
Contact:

Re: ATR144-ABC-T master serial port section missing

Post by Pixsys tecnico 1 »

Hi,
group L is hidden if you have enable the "Slave mode" in the group K, parameter 149 "Mb.SL.".
You can try also to reset the configuration to factory default using "9999" password instead of "1234".
Post Reply