DRR244-13ABC-T -- how to set relay 1 and 2

Posted: 17/04/2023, 17:50
by Davy
Dear Support

we got an DRR244-13ABC-T with Pt100 input.
We would like to have 2 relays, one NC and one NO.
We would like to set alarm value at 25°C.
when temperature is over 25°C, relay 1 should be open and relay 2 should be close.

the setting of input seems to work as we can read temperature.
we set in :
Group G
123 Ab.uP.A
126 N.c. St.
Group H
141 Ab.uP.A
144 N.o S.t

then when we change temperature, only relay 1 change is status .. not relay 2... why ?
kindly help

thanks and regards.
Davy.

Re: DRR244-13ABC-T -- how to set relay 1 and 2

Posted: 18/04/2023, 13:03
by Pixsys tecnico 6
Good morning,
Output Q1 is already enabled by default, so only output Q2 needs to be enabled from Par.123.
123 Ab.uP.A
126 N.o. St.
Parameters.jpg
Setpoint.jpg
Br

Re: DRR244-13ABC-T -- how to set relay 1 and 2

Posted: 18/04/2023, 17:33
by Davy
Hi tecnico 6

thanks for your reply, we do :
35 c.01
123 up.dev
141 up.dev

Thanks for your answer.