Dear Support
we got an DRR244-13ABC-T with Pt100 input.
We would like to have 2 relays, one NC and one NO.
We would like to set alarm value at 25°C.
when temperature is over 25°C, relay 1 should be open and relay 2 should be close.
the setting of input seems to work as we can read temperature.
we set in :
Group G
123 Ab.uP.A
126 N.c. St.
Group H
141 Ab.uP.A
144 N.o S.t
then when we change temperature, only relay 1 change is status .. not relay 2... why ?
kindly help
thanks and regards.
Davy.
DRR244-13ABC-T -- how to set relay 1 and 2
-
- Posts: 2
- Joined: 17/04/2023, 16:36
- Location: FRANCE
-
- Moderatore
- Posts: 1201
- Joined: 12/09/2016, 14:49
Re: DRR244-13ABC-T -- how to set relay 1 and 2
Good morning,
Output Q1 is already enabled by default, so only output Q2 needs to be enabled from Par.123.
123 Ab.uP.A
126 N.o. St.
Br
Output Q1 is already enabled by default, so only output Q2 needs to be enabled from Par.123.
123 Ab.uP.A
126 N.o. St.
Br
You do not have the required permissions to view the files attached to this post.
-
- Posts: 2
- Joined: 17/04/2023, 16:36
- Location: FRANCE
Re: DRR244-13ABC-T -- how to set relay 1 and 2
Hi tecnico 6
thanks for your reply, we do :
35 c.01
123 up.dev
141 up.dev
Thanks for your answer.
thanks for your reply, we do :
35 c.01
123 up.dev
141 up.dev
Thanks for your answer.
-
- Posts: 1
- Joined: 23/08/2024, 16:20
Re: DRR244-13ABC-T -- how to set relay 1 and 2
It's so clear! Thanks geometry dasha lot!