Iris _

Pixsys Forum

everybody's effort for the same goal

Heating cord connection to ATR244-12ABC

Post Reply
Sofia
Posts: 1
Joined: 18/08/2022, 13:19

Heating cord connection to ATR244-12ABC

Post by Sofia »

Hello,

We aquired a controller ATR244-12ABC and we are trying to connect a flexible heating cord from Selecta with two connecting wires (https://grupo-selecta.com/productos/cor ... os-1000781). Could you indicate the corresponding connection positions based on the wiring diagram numbers? We tried to connect it on numbers 1 and 4.
However, something is off because the temperature goes up when the setpoint is lower than the measured temperature.

Thank you for your help.

Best regards,
Sofia
Pixsys tecnico 6
Moderatore
Posts: 1218
Joined: 12/09/2016, 14:49

Re: Heating cord connection to ATR244-12ABC

Post by Pixsys tecnico 6 »

Good morning,
The flexible heating cord must be connected to pins 4-5 for the heating function.
The connection have be as follows:
From pin 1 of the thermoregulator go to pin 4.
From Pin 5 connect to the heating cord.
From pin 2 of the thermoregulator connect to the second wire of the heating cord.

Best regards