[ATR244-12ABC] ON/OFF setting parameters

Posted: 13/07/2022, 11:30
by Cb500pc32
Hello. I have ATR244-12ABC.

What is the relationship of par 47, 82 and 86?

Re: [ATR244-12ABC] ON/OFF setting parameters

Posted: 18/07/2022, 16:53
by Pixsys tecnico 6
Hi,
In par.47, set the valve opening time if the par.35 is set as the "c.val" valve control.
The par.82 is used to set the output cycle time (heat) only if par.75 and 76 are different from 0 and if the par.35 is set as "c.SSR" or "c.o1/2"
The par.86 is used to set output cycle time (cool) in "heating-cooling" mode only for Par.75 and 76 are different from 0 and if the par.35 is set as "c.SSR" or "c.o1/2" and par.123 [AL.1.F] is set as "cool".
You can find more information on page 21 of the manual in the attach.

Best Regards