[ATR244-12ABC] ON/OFF setting parameters

Post Reply
Cb500pc32
Posts: 3
Joined: 12/07/2022, 20:12

[ATR244-12ABC] ON/OFF setting parameters

Post by Cb500pc32 »

Hello. I have ATR244-12ABC.

What is the relationship of par 47, 82 and 86?
Pixsys tecnico 6
Moderatore
Posts: 1198
Joined: 12/09/2016, 14:49

Re: [ATR244-12ABC] ON/OFF setting parameters

Post by Pixsys tecnico 6 »

Hi,
In par.47, set the valve opening time if the par.35 is set as the "c.val" valve control.
The par.82 is used to set the output cycle time (heat) only if par.75 and 76 are different from 0 and if the par.35 is set as "c.SSR" or "c.o1/2"
The par.86 is used to set output cycle time (cool) in "heating-cooling" mode only for Par.75 and 76 are different from 0 and if the par.35 is set as "c.SSR" or "c.o1/2" and par.123 [AL.1.F] is set as "cool".
You can find more information on page 21 of the manual in the attach.