Iris _

Pixsys Forum

everybody's effort for the same goal

Programming ATR121-B module

Post Reply
lmh1190
Posts: 2
Joined: 28/07/2021, 13:51

Programming ATR121-B module

Post by lmh1190 »

Hi,

I have replaced an old ATR121-B module that is used for a powdercoating oven. It has been wired in and appears to be working correctly. However when I start up the oven, the burner unit will not kick in as the temperature module does not pick up the upper and lower temperatures as set on OUT 1 & OUT 2.

I understand I need to programme the parameters and configuration etc so I was wondering if someone could advise on what all of these need to be set to for our use? We need a maximum of 300 degrees

If it helps...
The oven is connected to a separate timer, that normally controls how long the oven is at a certain temperature. Once it reaches temperature the timer starts and OUT1 and OUT 2 are maintained for time period.
We currently have OUT1 set to 100 degrees c and OUT2 set to 90. but as soon as the oven is turned on to heat up, the timer kicks in at 20 degrees instead of heating up.
Pixsys tecnico 6
Moderatore
Posts: 1196
Joined: 12/09/2016, 14:49

Re: Programming ATR121-B module

Post by Pixsys tecnico 6 »

Good morning,
Could you explain the operation of out 1 and out 2?
What do the exits activate?
Out 1 is normally used for heating and Out 2 as an alarm that can be activated above or below the setpoint of Out 1.
lmh1190
Posts: 2
Joined: 28/07/2021, 13:51

Re: Programming ATR121-B module

Post by lmh1190 »

the operation of out1 and out 2 is to create a temperature range/band for curing powdercoated items. For example if we require the oven at 180 degrees for 15mins then we set out1 at 185 and out2 at 175. The oven heats up until it reaches 185, the burner then switches off until it drops to 175, when it kicks in again to heat back up to 185.
Pixsys tecnico 6
Moderatore
Posts: 1196
Joined: 12/09/2016, 14:49

Re: Programming ATR121-B module

Post by Pixsys tecnico 6 »

Good Morning,
What do Q1 and Q2 command?
Did you change any parameters in configuration?
Godinho
Posts: 1
Joined: 17/09/2021, 7:26

Re: Programming ATR121-B module

Post by Godinho »

Good morning Gents
I need your help for programming my ATR121-B
I have two news one, also connecting why'd PT100 and don't work, I was checking all connections are the same situation, on my opinion I thinking they need configuration or change some parameters for working why'd PT100 PROBE.
what do you think? can you help me?
Pixsys tecnico 6
Moderatore
Posts: 1196
Joined: 12/09/2016, 14:49

Re: Programming ATR121-B module

Post by Pixsys tecnico 6 »

Good morning,
Check that the links are correct as in the following picture:
image.png
Configure that parameter 2 [Sen] is set to "pt"
To enter the configuration follow the following steps:
image1.png
You do not have the required permissions to view the files attached to this post.
Post Reply