Page 1 of 1

[ATR401-22ABC-T] AO in Volt

Posted: 17/01/2012, 15:13
by user2366
hello

i want to store the actual temperature via labview (5V). therefore i put the jumper on jp3. but then i only get 0.011 V altough the temperature is increasing.
any ideas?

Re: AO in Volt - ATR401-22ABC-T

Posted: 18/01/2012, 8:47
by Pixsys tecnico 1
Hi,
if you want to retransmit the input signal in volt 0-10V, you have to set the following parameters:

[Sen] set the type of sensor
[rEtr] "Pro.1"
[LoLr] and [uPLr] as the lower and the upper limits for analog output for example:
Temperature form 0°C to 100°C --> 0V to 10V, [LoLr]:"0" and [uPLr]: "100"

You have also to put the jumper on jp3.

Re: AO in Volt - ATR401-22ABC-T

Posted: 18/01/2012, 13:09
by user2366
thanks... works perfect!