[ATR401-22ABC-T] Error E-5 on display

Posted: 04/01/2012, 10:32
by user2366
i have this error on display on power up.
i'm using a pixsys pt1000B. i tried it with 5 differnt pt1000s that i bought in the shop. (connection: white - 12, red - 13)
if i short the input the error is still on the display?
any ideas?
THX

Re: ATR401-22ABC-T: Error E-5 on display

Posted: 09/01/2012, 8:43
by Pixsys tecnico 1
Hi,
You have to connect the probe on 12 and 13, set the [SEN.1] parameter as "Pt1K" and check if the [SEn.2] parameter is set as "diS."

Re: ATR401-22ABC-T: Error E-5 on display

Posted: 09/01/2012, 12:16
by user2366
now it works.
i used the easyup code 2251 from the datasheet... any idea why it didn't work?

Re: ATR401-22ABC-T: Error E-5 on display

Posted: 09/01/2012, 14:15
by Pixsys tecnico 1
Probably the [SEn.2] parameter wasn't set as "dis" so the controller check also the second input that was disconnected.