ATR 142 Memory after Power Failure

Posted: 02/09/2019, 22:38
by Dod253
Evening all, first post and a query on the ATR 142 being used on a RO plant for Thermal disinfection every evening...
If controller is programmed at say 87oC and their is a power outage... how long will the controller retain its set point before it reverts to factory setting or does this not occur and controller retains its last setting..??

Re: ATR 142 Memory after Power Failure

Posted: 03/09/2019, 8:51
by Pixsys tecnico 6
Hi,
the value of the ATR142 Setpoint (and its parameters value) is stored in a EEPROM Memory. The EEPROM memory is not a Flash memory and the value is kept forever with power or not power suply actived.

Best Regards.