movicon issue with symbol file on startup

Posted: 01/08/2019, 10:22
by JamieP4A
All, I am currently using a TD710 HMI, when I try to run my movicon program, I am getting an error via a pop up on screen:
"Cannot validate symbol table at startup, please check symbol table path and connection to the PLC then restart"

I believe the issue is with paths in the stations settings in comm drivers, and it not auto-populating or copying the file over.

Any ideas, as this is very frustrating.

Re: movicon issue with symbol file on startup

Posted: 01/08/2019, 16:49
by Pixsys tecnico 6
Good morning,
in the links below follow tutorial number 4 and 5 where it shows how to correctly configure the Movicon Station and how to correctly import PLC variables.

https://forum.pixsys.net/viewtopic.php?f=25&t=1768

Best Regards.

Re: movicon issue with symbol file on startup

Posted: 02/08/2019, 10:14
by JamieP4A
Hi Pixsys tecnico 6, When I carry out the instructions in step 5, it does not copy the sym. xml file over to the HMI, even after I have uploaded the project. thoughts?

Thanks
Jamie

Re: movicon issue with symbol file on startup

Posted: 02/08/2019, 15:03
by Pixsys tecnico 6
Hi,
please check the LogicLab settings.
LogicLab_symbol_enabled.PNG
Can you post the Movicon Station configuration?

Best Regards.

Re: movicon issue with symbol file on startup

Posted: 02/08/2019, 15:21
by JamieP4A
Capture.PNG

Re: movicon issue with symbol file on startup

Posted: 05/08/2019, 11:52
by Pixsys tecnico 6
Hi,
please download an install the last version of the Movicon and PixsysSuite software at follow link:
1.https://cloud.pixsys.net/
Download_Mov_Log.PNG
2.Instal the last driver available:
Download_last_drivers.PNG
3. Close your Movicon Project and delete the follow files by your project RESOURCES folder.
Movicon_file_settings.PNG
4.Please check your Movicon Station settings. At follow picture there is a Typical settings:
Movicon_Station_conf.PNG
Best Regards.