Logic Lab Retain Memory Low
Posted: 10/07/2019, 16:21
by gothomas
Hi guys,
Having some issues with the retain memory lower than 10%
I have a very large program with lots of retain variables that are required.
the problem is that the program is not completed and im getting the error attached.
Any fix that?
Re: Logic Lab Retain Memory Low
Posted: 11/07/2019, 16:04
by Pixsys tecnico 6
Hi,
what type of TARGET are you using?
Best Regards.
Re: Logic Lab Retain Memory Low
Posted: 11/07/2019, 20:02
by gothomas
Hi,
The target im using for the project is a TD900.
Is it possible to increase the size of retain memory?
Thanks.
Re: Logic Lab Retain Memory Low
Posted: 12/07/2019, 14:22
by Pixsys tecnico 6
Hi,
It is possible to increase the size of retain memory, please follow the steps:
1. Stop LogicLab TD900 RunTime software.
2. Unzip the attached file (.conf) and copy it to D:\LLExec folder of the TD900.
3. Reboot the TD900.
4. Connect the LogicLab to the Target and try again to compile and download the software.
Best regards.
Re: Logic Lab Retain Memory Low
Posted: 12/07/2019, 15:44
by gothomas
Hi,
Thanks.
Is it the same file configuration that i use on the PC i am programming with?
Re: Logic Lab Retain Memory Low
Posted: 12/07/2019, 16:51
by Pixsys tecnico 6
Hi,
it is not same file. The conf file that I posted is different from what is default on TD900.
Best Regards.
Re: Logic Lab Retain Memory Low
Posted: 12/07/2019, 18:07
by gothomas
Hi,
Thanks for the file. It has done the job, programming can continue

Re: Logic Lab Retain Memory Low
Posted: 15/07/2019, 8:26
by Pixsys tecnico 6
Ok, thanks for your feedback.
Best Regards.