Controller ATR621-14ABC
-
user14957
- Posts: 3
- Joined: 28/03/2017, 13:40
Controller ATR621-14ABC
good afternoon! At our factory the controller ATR620 was out of order, we had to replace ATR621 with it. Please tell me how to transfer the settings of the old controller to a new one
-
Pixsys tecnico 6
- Moderatore
- Posts: 1214
- Joined: 12/09/2016, 14:49
Re: Controller ATR621-14ABC
Hi,
if you want to replace the ATR620 with the ATR621 you must set manually the parameters of the ATR621. There is not a automatic method to copy the old parameters in to a new ATR621, but the old parameters are the same of the new ATR621 parameters.
Best Regards
if you want to replace the ATR620 with the ATR621 you must set manually the parameters of the ATR621. There is not a automatic method to copy the old parameters in to a new ATR621, but the old parameters are the same of the new ATR621 parameters.
Best Regards
-
user14957
- Posts: 3
- Joined: 28/03/2017, 13:40
Re: Controller ATR621-14ABC
Thank you for helping us! We have so far managed to adjust the time and temperature and the inclusion of one group of heating tones until you get to activate the second and cooling mode
-
user14957
- Posts: 3
- Joined: 28/03/2017, 13:40
Re: Controller ATR621-14ABC
File with old settings ATR 620 is very different from ATR 621
You do not have the required permissions to view the files attached to this post.
-
Pixsys tecnico 1
- Moderatore
- Posts: 1730
- Joined: 29/10/2010, 10:09
- Contact:
Re: Controller ATR621-14ABC
Hi,
see the table attached (change only highlighted parameters, leave others as default).
see the table attached (change only highlighted parameters, leave others as default).
You do not have the required permissions to view the files attached to this post.